  1. #1
    New User
    Join Date
    Aug 2013
    Location
    Spring, TX
    Posts
    11

    Air Conditioner Never Shuts Off

    Basically I want the A/C in my fish room to run 2 hours on, 2 hours off from midnight to noon, then 3 hours on, 1 hour off from noon to midnight. Also to turn on any time the air temp of the room exceeds 79°F and run for a minimum of 30 minutes.

    Probe
    AirTmp

    Virtual Outlets
    OSC1
    OSC 000:00/120:00/120:00 Then ON
    If Time 11:59 to 23:59 Then OFF

    OSC2
    OSC 000:00/180:00/060:00 Then ON
    If Time 23:59 to 11:59 Then OFF

    EB4 physical outlet
    AC_4_2
    Fallback ON
    If Output OSC1 = ON Then ON
    If Output OSC2 = ON Then ON
    If AirTmp > 79.0 Then ON
    Min Time 000:30 Then OFF




    I can't figure out what I am doing wrong. Seems like the A/C never turns off...

    right now its 11:42. I see that OSC1 and OSC2 are both off, AC_4_2 is on and the probe is reporting air temp of the room to be 70.2°F

  2. #2
    Frequent Visitor rkpetersen's Avatar
    Join Date
    Jun 2017
    Location
    Near Seattle
    Posts
    940
    Couple things. You need a Set OFF statement after Fallback ON to turn it off. Otherwise once it turns on it won't ever turn off again.

    Also it's best not to overlap time periods. So I might change the first to 12:00 to 23:59 and the second one to 00:00 to 11:59.

  3. #3
    New User
    Join Date
    Aug 2013
    Location
    Spring, TX
    Posts
    11
    I just added Set OFF and its seems the port was turned off.



    Fallback ON
    Set OFF
    If Output OSC1 = ON Then ON
    If Output OSC2 = ON Then ON
    If AirTmp > 79.0 Then ON
    Min Time 000:30 Then OFF

  4. #4
    New User
    Join Date
    Aug 2013
    Location
    Spring, TX
    Posts
    11
    Quote Originally Posted by rkpetersen View Post
    Couple things. You need a Set OFF statement after Fallback ON to turn it off. Otherwise once it turns on it won't ever turn off again.

    Also it's best not to overlap time periods. So I might change the first to 12:00 to 23:59 and the second one to 00:00 to 11:59.
    Thanks. I actually just realized I was being a dummy. Thanks for the reply and the info about timing overlap. I changed that as well.

  5. #5
    Frequent Visitor rkpetersen's Avatar
    Join Date
    Jun 2017
    Location
    Near Seattle
    Posts
    940
    There you go. Check your OSC VOs to see whether you should be getting air right now. And don't forget that, the way you have it, it can't automatically come on again for at least 30 seconds.

    Edit: posted this before I saw your last reply. (And also corrected my own senior moment.)

Similar Threads

  1. Help! New cor 15 shuts down system
    By Montdj in forum COR-15 & COR-20 Pumps
    Replies: 4
    Last Post: 11-28-2020, 14:35
  2. reading salinity/conditioner probe
    By tableforglasses in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 7
    Last Post: 12-27-2018, 07:20
  3. Help! MP40 Shuts off after about a minute
    By RiderintheReef in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 3
    Last Post: 09-05-2016, 16:04
  4. Question: APEX shuts off on it own....
    By Eyesell in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 2
    Last Post: 12-27-2015, 19:45
  5. Help! DOS Shuts off system
    By Detlev in forum DŌS & DDR – Dosing and Fluid Metering System
    Replies: 3
    Last Post: 12-18-2015, 21:18

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •