    Apex, third world problems, first world solutions

    Hi, I have the Apex 2016 with the old EB6 from the EU. I want to know if there is a way to connect the brain to the UPS to keep running and the EB6 to the normal wall power supply. If there is a power failure, the brain will keep running and the EB6 will cut out. I then would like to have the Brain tell me via email that the brain and EB6 have lost connection. Is this possible and what is the code?

  2. #2
    Frequent Visitor
    Join Date
    May 2014
    Location
    Portugal
    Posts
    389
    Yes there is ...
    you just need to connect a 12v power supply to the auxilary power (2.1mm tip, 12V input ,0.7A DC output with a center positive electrode (Use Neptune P/N PS12)) and connect that power supply to the UPS while maintaining the EB6 to the wall.

    then insert this in your email alarm outlet
    If Power EB8_5 (the address of your EB) 000 Then ON

    Hope this helps.
    Rui

  3. #3
    Frequent Visitor rkpetersen's Avatar
    Join Date
    Jun 2017
    Location
    Near Seattle
    Posts
    940
    I don't have an older Apex to compare but shouldn't the power failure code to put in your text email be: If Power [EnergyBar] Off 000 Then ON ?

  4. #4
    Frequent Visitor
    Join Date
    May 2014
    Location
    Portugal
    Posts
    389
    From the old comprehensive manual ...

    The most common usage of the ‘If Power’ statement where no duration delay is used is for an Email alert. In this
    case, you typically don’t want power failure notifications AFTER power is restored. In that case, a ‘0’ delay is used
    Page 57 Version: 5.0
    in the Email outlet. However, if you don’t have supplemental 12v power, adding a 1 minute delay will get you your
    email message once power is turned back on.
    If Power EB8_5 000 Then ON  use when you have supplemental 12v power available
    If Power EB8_5 001 Then ON  use when you don’t have any other power source
    This sets the Email outlet register to ON as soon as power goes out. When power returns, the outlet state goes to
    OFF as soon as the delay (000 or 001) is satisfied.

  5. #5
    Regular Vistor
    Join Date
    Apr 2018
    Location
    Namibia
    Posts
    16
    Hi Rui,

    Is this for the normal British power or American power supply voltage? We run 240 volts here.

    And why must I put in If Power EB8_5 (the address of your EB) 000 Then ON
    If I have the EB6? We dont get the EB8.

    Hope to hear from you soon

  6. #6
    Frequent Visitor
    Join Date
    May 2014
    Location
    Portugal
    Posts
    389
    You need to go to your classic dashboard and in the modules section understand what is your address name. it should be EB(something)_(address) ... that's the value you need to use.

    I only have the EB8 and not an EB6 so I don't know how it's represented in the module.

    But you can quickly check!

  7. #7
    Regular Vistor
    Join Date
    Apr 2018
    Location
    Namibia
    Posts
    16
    Classic dashboard? I only know the normal Apex Fusion dashboad.

  8. #8
    Fish Whisperer cypherljk's Avatar
    Join Date
    Oct 2013
    Location
    Charlotte, NC
    Posts
    442
    A presentation that Russ did on setting up for power outages and handling them: https://forum.neptunesystems.com/sho...n-at-MACNA2013

  9. #9
    Frequent Visitor
    Join Date
    May 2014
    Location
    Portugal
    Posts
    389
    sorry ... my bad.
    That's fine with the APEX 2016.

    in fusion go to the gear icon and then select modules you will have the energy bars described. Check the type and address.
    if you haven't changed the name, then the name it's the value you need to use.

    All the best,
    Rui

  10. #10
    Frequent Visitor rkpetersen's Avatar
    Join Date
    Jun 2017
    Location
    Near Seattle
    Posts
    940
    Quote Originally Posted by Rui Manuel Gaspar View Post
    From the old comprehensive manual ...

    The most common usage of the ‘If Power’ statement where no duration delay is used is for an Email alert. In this
    case, you typically don’t want power failure notifications AFTER power is restored. In that case, a ‘0’ delay is used
    Page 57 Version: 5.0
    in the Email outlet. However, if you don’t have supplemental 12v power, adding a 1 minute delay will get you your
    email message once power is turned back on.
    If Power EB8_5 000 Then ON  use when you have supplemental 12v power available
    If Power EB8_5 001 Then ON  use when you don’t have any other power source
    This sets the Email outlet register to ON as soon as power goes out. When power returns, the outlet state goes to
    OFF as soon as the delay (000 or 001) is satisfied.

    I'm looking at that now and wondering if it's a typo that wasn't caught. Several other places in the manual include the word OFF, such as here:

    Clipboard05.jpg

    One test though is to try and upload the code without the word 'Off'. At least on the 2016 model with current AOS, this results in a Send Fail.

    Apologies again if this does not pertain to older models and other firmware.

  11. #11
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    RK and RUI were correct. You should use

    If Power EB6name Off 000 Then ON

    In your email. The power apex statement means the apex rebooted if power monitoring is disabled and 12V aux supply is dead if power monitoring is enabled.

    Sent from my SM-G965U using Tapatalk

  12. #12
    Regular Vistor
    Join Date
    Apr 2018
    Location
    Namibia
    Posts
    16
    Quote Originally Posted by zombie View Post
    RK and RUI were correct. You should use

    If Power EB6name Off 000 Then ON

    In your email. The power apex statement means the apex rebooted if power monitoring is disabled and 12V aux supply is dead if power monitoring is enabled.

    Sent from my SM-G965U using Tapatalk
    Ok, but where I am we can't do power monitoring as when we buy the Apex system we get the 2016 brain but with the older EB6 power brick. which SUX
    My question is not really about power loss reports, but if the Apex and the EB6 looses communication. What is that code?

    It is a way that I think I can get an alert without having the ability to do power monitoring.

    The Idea I got looking at a presentation that Russ did on setting up for power outages and handling them slide show, Have a look and let me know if this might workApex on UPS only.png

  13. #13
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    The power monitoring setting has nothing to do with amps or watts despite the misleading name. It changes the behavior of how the if power Apex statement works. Use the eb6 power statement.

    Sent from my SM-G965U using Tapatalk

  14. #14
    Frequent Visitor
    Join Date
    May 2014
    Location
    Portugal
    Posts
    389
    Quote Originally Posted by FvdB View Post
    Ok, but where I am we can't do power monitoring as when we buy the Apex system we get the 2016 brain but with the older EB6 power brick. which SUX
    My question is not really about power loss reports, but if the Apex and the EB6 looses communication. What is that code?

    It is a way that I think I can get an alert without having the ability to do power monitoring.

    The Idea I got looking at a presentation that Russ did on setting up for power outages and handling them slide show, Have a look and let me know if this might workApex on UPS only.png
    This schema was exactly what I was telling you in the first post. Tomorrow I will try in mine and post here the results


    Sent from my iPhone using Tapatalk

Similar Threads

  1. Replies: 0
    Last Post: 08-09-2021, 10:02
  2. MSDS for Calibration Solutions
    By RayKCMO in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 2
    Last Post: 04-03-2018, 15:20
  3. Calibration solutions
    By flowerseller in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 1
    Last Post: 11-04-2017, 18:36
  4. pH calibration solutions--where to get them?
    By jeff67 in forum Misc Aquarium Automation Discussions
    Replies: 3
    Last Post: 11-17-2014, 20:02

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •