HI,
I have just installed a WXM and my 2 pumps are showing 0% in the dash board but the keep switching randomly on and off may be every 20 seconds or so at 100% anyone got a idea what is causing this?
HI,
I have just installed a WXM and my 2 pumps are showing 0% in the dash board but the keep switching randomly on and off may be every 20 seconds or so at 100% anyone got a idea what is causing this?
Click on the Basic View, and post the configuration.
And why do you have them set to 0%? That turns them OFF.
Thanks for the quick response.
I had them set to off to prove it was producing flow when it was not meant to.
when I switch them from auto to the on position theScreenshot 2018-07-26 18.02.32.jpg
Screenshot 2018-07-26 18.02.32.jpg
What I was looking for is the programming.
On the top left tiles, click the that looks like a list. It's the one to the right of the one that looks like an outlet.
MP40.JPG
MP40config.JPG
thanks,
I think I cracked it!! my GHL controller still had power to it and I think it was interfering with the drivers
I had two tanks, different rooms ~ 50' apart, both Apex controlled, both running WXM's and MP40's, I couldn't figure out for the life
of me why even though they didn't show up on the other controller, why the were doing crazy things. I had to change the frequency