I'm setting up a VarioS-8 return pump with 0-10V control.
I want to do something like this:
Fallback ON
Set Ramp000080
If FeedA 000 Then Ramp080030
But after feed mode I want to ramp from 30% back to 80% and not drop down to 0%. Can I do this?
I'm setting up a VarioS-8 return pump with 0-10V control.
I want to do something like this:
Fallback ON
Set Ramp000080
If FeedA 000 Then Ramp080030
But after feed mode I want to ramp from 30% back to 80% and not drop down to 0%. Can I do this?
I would just make your set ramp 30 to 80. The quick jump from 0 to 30 is actually better for the pump than ramping from 0 since it will be stalled less time.
Sent from my SM-G965U using Tapatalk
Soft starts are better, but the power delivered between 0-30% is often not enough to even move the impeller, and stalling is worse than quick starts to low intensities. A jump from 0-30 immediately is better than a ramp from 0-30 and both are better than a jump from 0-100.
Sent from my SM-G965U using Tapatalk