    SV-1 for ATO Resevoir





    I知 trying to setup my SV-1 to trigger on when lower water is triggered and run until high water is triggered.

    I would also like to add a run timer that will shut it if after 10 minutes (times it takes to fill up my high tech ATO container)


    Sent from my iPhone using Tapatalk

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    11,278
    Rename your switches to something meaningful in the inputs tab. Install a mechanical float as a backup in case the solenoid ever fails.

    Fallback OFF
    If lowRES OPEN Then ON
    If highRES CLOSED Then OFF
    Defer 000:10 Then ON
    Defer 000:04 Then OFF
    When On > 010:00 Then OFF

    Email
    If Error SolenoidName Then ON

    Sent from my SM-G965U using Tapatalk

  3. #3
    New User
    Join Date
    Apr 2018
    Location
    Arizona
    Posts
    7
    Thanks! Yeah once I get a better container I値l set up a float on a break out box.


    Sent from my iPhone using Tapatalk

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    11,278
    Quote Originally Posted by SteveD1974 View Post
    Thanks! Yeah once I get a better container I値l set up a float on a break out box.


    Sent from my iPhone using Tapatalk
    I was actually referring to a valve not a switch like this.

    https://www.bulkreefsupply.com/ro-fl...saArWaEALw_wcB

    Sent from my SM-G965U using Tapatalk

  5. #5
    New User
    Join Date
    Apr 2018
    Location
    Arizona
    Posts
    7
    Okay, I知 at a loss. Copied over the programming as advised but as soon as I set to auto the Solenoid opens. Thoughts?

    The other issues I have, if I trigger the Solenoid on and then go to auto it keeps running. I have to move to off and then auto to shut it off.






    Sent from my iPhone using Tapatalk

  6. #6
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    11,278
    Quote Originally Posted by SteveD1974 View Post
    Okay, I知 at a loss. Copied over the programming as advised but as soon as I set to auto the Solenoid opens. Thoughts?

    The other issues I have, if I trigger the Solenoid on and then go to auto it keeps running. I have to move to off and then auto to shut it off.






    Sent from my iPhone using Tapatalk
    That is expected. Drop the high sensor under water and you will see it shut off and stay off until the low sensor is above water.

    Sent from my SM-G965U using Tapatalk

  7. #7
    New User
    Join Date
    Apr 2018
    Location
    Arizona
    Posts
    7


    As you can see both closed and Solenoid still on.


    Sent from my iPhone using Tapatalk

  8. #8
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    11,278
    Quote Originally Posted by SteveD1974 View Post


    As you can see both closed and Solenoid still on.


    Sent from my iPhone using Tapatalk
    Did you keep them both closed for at least 4 seconds? There is a defer in there for filtering.

    Sent from my SM-G965U using Tapatalk

  9. #9
    New User
    Join Date
    Apr 2018
    Location
    Arizona
    Posts
    7
    I moved the high water level sensor below the water line and left for much longer than 4 seconds. I also tried removing the defer line completely


    Sent from my iPhone using Tapatalk

  10. #10
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    11,278
    Did you hear the solenoid click after the 4 seconds? Fusion updates every 30 seconds or so, so there can appear to be a delay when there actually isnt.

    Sent from my SM-G965U using Tapatalk

  11. #11
    New User
    Join Date
    Apr 2018
    Location
    Arizona
    Posts
    7
    Pulled the higRES sensors above the water line and watched Fusion switch to open and 10 seconds later the Solenoid opened.

    Moved the higRES sensor below the water line and I see Fusion move to close but the Solenoid doesn稚 trigger to close.


    Sent from my iPhone using Tapatalk

  12. #12
    New User
    Join Date
    Apr 2018
    Location
    Arizona
    Posts
    7
    Scratch that, had the programming looking the the wrong optic sensor.

    Thanks for all your help!!


    Sent from my iPhone using Tapatalk

  13. #13
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    11,278
    Quote Originally Posted by SteveD1974 View Post
    Pulled the higRES sensors above the water line and watched Fusion switch to open and 10 seconds later the Solenoid opened.

    Moved the higRES sensor below the water line and I see Fusion move to close but the Solenoid doesn稚 trigger to close.


    Sent from my iPhone using Tapatalk
    That is expected. You have to open the low sensor to get it to turn back ON.

    Sent from my SM-G965U using Tapatalk