Thread: Getting alerts about low wattage on canister filter

  1. #1
    Regular Vistor
    Join Date
    Sep 2018
    Location
    EST
    Posts
    43

    Getting alerts about low wattage on canister filter

    I keep getting alerts that the Watts have fallen below my preset limit for my canister filter. When i review the power log the Watts are still within the tolerances i have specified and should not be getting an alert. I even dropped the lower limit down alot further and am still geting these alerts. Is this a bug in the apex system because i can clearly see the Watts have not fallen below the limit I have set. This has happened many, about 8 times over the last three days. I will get an alert and then immediatly ~1 minute later i will get another alert saying the first is cleared and it is above the limit again. Im using the eb832 on apexel.

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    It's probably transient drops that just don't happen long enough for them to still be present when you check. You could adjust the threshold or remove them from the input alarm and add the watts statement to your email with a longer defer (input alarms are all 10 second defer).

    Sent from my SM-G965U using Tapatalk

  3. #3
    Regular Vistor
    Join Date
    Sep 2018
    Location
    EST
    Posts
    43
    Thanks. Could this mean that the canister filter is going bad or is this normal to see?
    So would the code look like:
    1. SET OFF
    2. Can_Filter Watts < 20
    3. Defer 001:00
    4. SET ON

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by jordanM View Post
    Thanks. Could this mean that the canister filter is going bad or is this normal to see?
    So would the code look like:
    1. SET OFF
    2. Can_Filter Watts < 20
    3. Defer 001:00
    4. SET ON
    It could very well indicate a problem with the canister filter. I would disassemble and clean it if you haven't already done so.

    The code for a delayed wattage is

    CanLowWatts (VO)
    Set OFF
    If Output Can_Filter Watts < 20 Then ON
    Defer 001:00 Then ON

    Email
    (Existing code)
    If Output CanLowWatts = ON Then ON

    Sent from my SM-G965U using Tapatalk

  5. #5
    Regular Vistor
    Join Date
    Sep 2018
    Location
    EST
    Posts
    43
    Thanks I gave that a try! The canister is a Fx4. I also have this running through some media block containers so i dont want to take it offline for to long and have the bacteria die.

  6. #6
    Regular Vistor
    Join Date
    Sep 2018
    Location
    EST
    Posts
    43
    Found out that the FX4 automatically turns off for a few seconds to a minute every day to purge out any air trapped in it. That is when i get the alerts about the low wattage. So far after switching the email code I have not got an alert yet so I think it is good.

Similar Threads

  1. Cor-20 to run large external canister filter?
    By clintonsparsons in forum Pre-Sales Questions
    Replies: 0
    Last Post: 07-02-2018, 07:21
  2. EB832 and low wattage devices
    By Tha Bizness in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 1
    Last Post: 02-07-2017, 13:50
  3. Question: Can an Apex be used to control a canister filter?
    By surfacetoorbit in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 3
    Last Post: 09-17-2016, 12:10
  4. low wattage equipment on EB8
    By Spar in forum Apex Classic/Apex Lite/Apex Jr
    Replies: 4
    Last Post: 11-08-2015, 11:29
  5. Outlets won't shut off, not low wattage
    By Hobbzz in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 27
    Last Post: 10-05-2014, 18:38

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •