    Dimming T5 and switching off

    Hi reef friends,

    I would like to switch my T5 lights with dimmable ballasts. Currently I use a GHL EVG-AP-2F-HIC print with my profilux to dimm them. Recently I switched to Apex and I would like the dimming feature.

    What I have;

    2 x 54W dimmable armatures ( I've got two of them, thus 3 x 54W)
    1 dimmable Neptune Apex cable

    Questions;
    1. Can I dimm both armatures with one dimming cable? I think only at the same time with one cable, right? Or because there are 4 cables (black, red, green and yellow) I can use one pair (black/red) for the first armature and one pair (green/yellow) for dimming the other unit?
    2. Do I put the power cable of both units in the EB6 to switch them completely off? Or can I switch them off with the Apex 0-10V ports? And thus save a port on my EB6?


  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    You can parallel or daisy chain the varspd to use one port for both lights if you want.

    Some T5 dont turn off completely at 0%. If yours does turn off, you don't need to plug into an energy bar. If yours don't turn off completely, you can use an outlet splitter to only use one outlet instead of two.

    Sent from my SM-G965U using Tapatalk

  3. #3
    New User
    Join Date
    Sep 2018
    Location
    Nederland
    Posts
    9
    Quote Originally Posted by zombie View Post
    You can parallel or daisy chain the varspd to use one port for both lights if you want.

    Some T5 dont turn off completely at 0%. If yours does turn off, you don't need to plug into an energy bar. If yours don't turn off completely, you can use an outlet splitter to only use one outlet instead of two.

    Sent from my SM-G965U using Tapatalk
    Thanks! I have made box that is powered separately en with waterproof connectors both armatures are powered. So I only need one outlet. So that is no problem. If I remember correctly I can't switch them off completely at 0%. That part (switch off) was done by the GHL print I used. A relay switched off when it needed to cut the power at 0%.

    Thanks for your reply!

Similar Threads

  1. Question: switching networks
    By richsfishes in forum Misc Apex Usage & Programming
    Replies: 1
    Last Post: 05-13-2020, 09:27
  2. Switching Out MP40s
    By Reefnut in forum Apex Programming for Vortech, Tunze, & Other Controllable Pumps
    Replies: 4
    Last Post: 12-19-2018, 20:12
  3. ATO switching off
    By Sevitz5 in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 1
    Last Post: 10-10-2018, 19:07
  4. Help! LED 1-10v Dimming doesn't go lower then 4v instead of 1 volt when dimming down.
    By Greendigger in forum Apex Programming for Lighting
    Replies: 1
    Last Post: 04-16-2018, 08:20
  5. Switching Dosing to 24/7
    By jtbgonesailing in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 3
    Last Post: 02-08-2013, 14:44

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •