I have a smart ATO connected to my energy bar, question is
Is there a way to double code it like if salinity <32 off and if it runs longer than X minutes then off
I have a smart ATO connected to my energy bar, question is
Is there a way to double code it like if salinity <32 off and if it runs longer than X minutes then off
The cond is easy. Just add this
If cond < 33 Then OFF
Min Time 030:00 Then OFF
Detecting run time is much more complex with a standalone ATO and requires a VO like this where X is a wattage between what it reads when not running and what it reads when running
ATOtimer
Set OFF
If Output Outletname Watts > X Then ON
When On > 005:00 Then ON
Add this to the ATO
If Output ATOtimer = ON Then OFF
Add this to email
If Error ATOtimer Then ON
Sent from my SM-G965U using Tapatalk
Min Time 030:00 Then OFF
What about turning back on? does it have to be manual or more code?
The outlet must be in auto to run your program.
Min Time is to prevent short cycling. The line says if the outlet turns off it must stay off for at least 30 minutes no matter what.
The lines and VO I gave were addition to your existing program. If you don't have an existing program, the whole thing would be
ATOtimer (VO)
Set OFF
If Output Outletname Watts > X Then ON
When On > 005:00 Then ON
ATO outlet
Fallback OFF
Set ON
If cond < 33 Then OFF
If Output ATOtimer = ON Then OFF
Min Time 030:00 Then OFF
Sent from my SM-G965U using Tapatalk