It can be done, but I prefer a different approach myself. What I do is have my heaters alternate under normal conditions, both run if one can't keep up, and when there is a loss of comms or obviously low temp only one runs. Both heaters have internal thermostats set 2 degrees above normal tank temp as an additional layer of protection. Below is an example
Heater1
Fallback ON
If Temp < 78.0 Then ON
If Time 00:00 to 11:59 Then OFF
If Temp < 77.8 Then ON
If Temp > 78.1 Then OFF
Heater 2
Fallback OFF
If Temp < 78.0 Then ON
If Time 12:00 to 23:59 Then OFF
If Temp < 77.8 Then ON
If Temp > 78.1 Then OFF
If Temp < 75.0 Then OFF