Thread: ATO Setting off Alarm

  1. #1
    Jens.k Jens.k's Avatar
    Join Date
    Aug 2018
    Location
    Copenhagen GMT +1
    Posts
    33

    ATO Setting off Alarm

    My ATO in Setting off alarm all the time this is my program What to charge? And what code line's i dont need?
    This is the alarm
    Date: 2018-10-25 23:36:45 +0200
    Status: ON
    Statement: If Swx5_2 CLOSED Then ON

    My
    program on the alarm
    Set OFF
    If Tmp > 26.0 Then ON
    If Tmp < 23.0 Then ON
    If Salt > 35.0 Then ON
    If Salt < 30.0 Then ON
    If pH > 8.50 Then ON
    If pH < 7.80 Then ON
    If ORP > 450 Then ON
    If ORP < 330 Then ON
    If Swx5_1 OPEN Then ON
    If Error ATO-A_5_1 Then ON
    If Swx5_2 CLOSED Then ON
    If Swx5_3 OPEN Then ON
    My program on the ATO
    Fallback OFFSet OFF
    If Swx5_1 OPEN Then ON
    If Swx5_2 CLOSED Then OFF
    If Swx5_3 OPEN Then OFF
    When On > 005:00 Then OFF
    Defer 000:10 Then ON
    Defer 000:04 Then OFF
    Min Time 060:00 Then OFF
    Skærmbillede 2018-10-26 kl. 01.19.31.png
    jens.k

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    You should rename your switches to something meaningful like ATOlow ATOhigh and RESlow.

    You should not have a line in your email for your lower switch opening.

    You need to determine why your high level switch is being covered. Is it during feeding or some other scenario your return is being turned off intentionally?

    Sent from my SM-G965U using Tapatalk

  3. #3
    Jens.k Jens.k's Avatar
    Join Date
    Aug 2018
    Location
    Copenhagen GMT +1
    Posts
    33
    The high level switch is not covered intentionally it not feeding i can't see why the high level switch is being covered / closed. maybe i shall run the programing one more time?
    i can not
    switch the ATOhig so it's on open.
    now is the
    switch 1 = ATOlow and the switch 2 = ATOhig switch 3 RESlow and i deleted the line in my Email so im good there.
    jens.k

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Are you saying the low sensor is reading closed no matter what even when the water level is below it?

    Sent from my SM-G965U using Tapatalk

  5. #5
    Jens.k Jens.k's Avatar
    Join Date
    Aug 2018
    Location
    Copenhagen GMT +1
    Posts
    33
    Yes i do
    jens.k

  6. #6
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    That often means the connector wasn't pressed in all the way and can also mean the optical sensor has failed (though the latter is much less likely).

    Sent from my SM-G965U using Tapatalk

  7. #7
    Jens.k Jens.k's Avatar
    Join Date
    Aug 2018
    Location
    Copenhagen GMT +1
    Posts
    33
    If the optical sensor has failed then i will clean then and start a new program. Schall the optical sensor be below water or up and dry when i start to program
    jens.k

  8. #8
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Jens.k View Post
    If the optical sensor has failed then i will clean then and start a new program. Schall the optical sensor be below water or up and dry when i start to program
    It makes no difference whether the sensor is dry or wet when you program. The code you showed above was fine as is and doesn't need to be reprogrammed. You may need to make modifications to the when, defer, and/or min time statement lengths if you have a very large or very small sump, however, those values usually work well for the majority of users.

    Sent from my SM-G965U using Tapatalk

  9. #9
    Jens.k Jens.k's Avatar
    Join Date
    Aug 2018
    Location
    Copenhagen GMT +1
    Posts
    33
    You did a nice job helping me Ty It seems that the sensor were dirty. and is seems im not geting the Alarm Email anymore.
    Skærmbillede 2018-10-27 kl. 22.07.23.png
    I Have a small sump is about 16 gal to a 52 gal Akvarium. any idea about the. defer, and/or min time ?
    Tank you so much for you help Zombie
    jens.k

  10. #10
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Jens.k View Post
    You did a nice job helping me Ty It seems that the sensor were dirty. and is seems im not geting the Alarm Email anymore.
    Skærmbillede 2018-10-27 kl. 22.07.23.png
    I Have a small sump is about 16 gal to a 52 gal Akvarium. any idea about the. defer, and/or min time ?
    Tank you so much for you help Zombie
    Check your output log. The defers should be fine but if you notice that the ATO only turns on for like 30 seconds at a time typically, then you can drop the when statement time to 2-3x the longest run in a 24 hour test period.

    Sent from my SM-G965U using Tapatalk

  11. #11
    Jens.k Jens.k's Avatar
    Join Date
    Aug 2018
    Location
    Copenhagen GMT +1
    Posts
    33
    Sorry Zombi This i dont understand : then you can drop the when statement time to 2-3x the longest run in a 24 hour test period.
    i need to understand what i shall do becours when Hig and low is open there not
    running water ?
    Fallback OFF
    Set OFF
    If ATOlow OPEN Then ON
    If ATOhig CLOSED Then OFF
    If RESlow OPEN Then OFF
    When On > 005:00 Then OFF ( is this my statement) And i shall make this run 2 or 3 times longer ? like 015:00 )
    Defer 000:10 Then ON
    Defer 000:04 Then OFF
    Min Time 060:00 Then OFF
    jens.k

  12. #12
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Jens.k View Post
    Sorry Zombi This i dont understand : then you can drop the when statement time to 2-3x the longest run in a 24 hour test period.
    i need to understand what i shall do becours when Hig and low is open there not
    running water ?
    Fallback OFF
    Set OFF
    If ATOlow OPEN Then ON
    If ATOhig CLOSED Then OFF
    If RESlow OPEN Then OFF
    When On > 005:00 Then OFF ( is this my statement) And i shall make this run 2 or 3 times longer ? like 015:00 )
    Defer 000:10 Then ON
    Defer 000:04 Then OFF
    Min Time 060:00 Then OFF
    If the pump has ran less than 1 hour ago and both sensors open, it will not run until an hour has passed. This is normal behavior.

    What I am saying about the When statement is to look at your outlet log for the pump or in the graph view select the ATO pump (make you you click the enable logging checkbox on the outlet). From there you can see how long your ATO pump ran each time it filled. Take the longest time you see in one day, and multiply that number by 3. That should be the length of the when statement.

    Sent from my SM-G965U using Tapatalk

Similar Threads

  1. Help! Setting up alarm when skimmer’s off
    By PacsAdmin in forum Misc Apex Usage & Programming
    Replies: 3
    Last Post: 05-06-2021, 08:03
  2. Alarm Setting Question
    By kayceejake in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 12
    Last Post: 01-24-2019, 15:13
  3. Question: setting alarm for temp
    By Bruce0462 in forum APEX Fusion
    Replies: 1
    Last Post: 11-16-2018, 08:46
  4. text alarm setting
    By Jtaylor1101 in forum APEX Fusion
    Replies: 9
    Last Post: 04-19-2015, 07:52
  5. Help! Setting up a Conductivity alarm
    By leeba in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 7
    Last Post: 08-05-2014, 11:53

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •