    Help with orp configuration

    Hi, i bought a used apex,I installed everything and in the screen of the fusion showed ph 2 instead orp, I changed the name but it is marking orp 2.62, what i can do?

  2. #2
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,463
    Renaming does not change the function. To switch the 2nd BNC port to ORP mode, just enable ORP using the Classic Dashboard.

    go to Configuration->Input setup, select the ORP port and enable it. PH2 will automatically be disabled when you do that.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

Similar Threads

  1. apex alarm for ORP....but im not using ORP!
    By Ron Popeil in forum Misc Apex Usage & Programming
    Replies: 1
    Last Post: 12-04-2018, 19:23
  2. Question: Local Output Configuration vs Fusion Output Configuration 2016
    By FoxTalbott in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 2
    Last Post: 11-07-2017, 06:39
  3. Missing ORP reading on display module and ORP alarm after power failure
    By Maroun.c in forum Misc Apex Usage & Programming
    Replies: 1
    Last Post: 03-01-2017, 22:29
  4. Question: Apex is reading ORP but I dont have an ORP Probe... Why?!?!
    By kyroshi in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 3
    Last Post: 02-18-2014, 12:19
  5. My graphs show orp reading but I don't have a orp probe!
    By Kisersozey in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 2
    Last Post: 12-19-2013, 14:05

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •