Where can I find info on having the ATK turn off as well as any alarms and warning when the feed mode is enabled?
Sent from my SM-N960U using Tapatalk
Where can I find info on having the ATK turn off as well as any alarms and warning when the feed mode is enabled?
Sent from my SM-N960U using Tapatalk
Turning off the ATK during feed is unnecessary since the water level will raise and turn it off anyway.
To supress alarms like the high level switch, you need a VO instead of the switch line in the email like this
HighSump
Set OFF
If HighSw CLOSED Then ON
If Output ReturnName = OFF Then OFF
Defer 005:00 Then ON
Replace switch line with
If Output HighSump = ON Then ON
Sent from my SM-G965U using Tapatalk
I am new to programming the APex but I need to figure this out as well. Can I get some beginner instructions on how to do this? Also, does this disable the alarm all the time or just when feed cycle is activated. I didn’t see any code that specify’s feed cycle.
Ok, my return pump does not shut down completely when I run feed mode, it just drops to a low percentage. I created a VO called ATK_Feed, what do I need to put in programming to disable alarm when FeedA is on and then what do I change in my alarm setting? Thanks for your help.