Thread: eb832 and 1link WAV problem

  1. #1
    Regular Vistor
    Join Date
    Nov 2018
    Location
    Ontario, Ca.
    Posts
    16

    eb832 and 1link WAV problem

    Hello
    I have a new Apex (2016 full) hooked up and running perfectly for a week now. Today I bought some additional Apex accessories and not having very good luck thus far.

    A) I bought two WAV pumps. If I plug either into any one of the three 1link ports on the eb832 then the eb832 will turn on all the outlets and flash orange after a short delay. Fusion is rendered useless and I'm unable to control anything. Fusion shows the eb832 as disconnected.
    How can I control the three link outlets? on/off

    B) I bought a leak detection kit. It's plugged in and has a solid green light. I see nothing on Fusion and I don't think anything works. That's two leak sensors and a optical sensor in my ato reservoir.

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Go to the modules page and update all of your module firmwares. Then try plugging the WAVs in one at a time. If you still have the same behavior, contact support.

    For the FMM, make sure you plug the connectors in all the way until you hear an audible click. This takes a bit of force. Then go to the module configuration for the FMM and verify that it detected the proper sensor type. If it did, the tiles are likely hidden in the unused tile bin area.

    Sent from my SM-G965U using Tapatalk

  3. #3
    Regular Vistor
    Join Date
    Nov 2018
    Location
    Ontario, Ca.
    Posts
    16
    I made have caused the failure.
    Under the dark stand, I managed to plug a 1link in backwards. (it will go with the safety tab inserting into a 24VDC port.)
    Just for a second but long enough to make the eb832 go crazy.

  4. #4
    Regular Vistor
    Join Date
    Nov 2018
    Location
    Ontario, Ca.
    Posts
    16
    I've got the FMM working now. Fusion shows the open/closed positions. I'm not getting notifications but I should be able to sort that out.

  5. #5
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Car2n View Post
    I've got the FMM working now. Fusion shows the open/closed positions. I'm not getting notifications but I should be able to sort that out.
    You have to add the alarms and lines to turn off anything relatively to the sensors. They are not plug and play.

    If LeakName CLOSED Then ON (or OFF)

    Is the format for the leak sensors. They are CLOSED when a leak is detected.

    The optical works similarly and that is CLOSED when covered in water.

    Sent from my SM-G965U using Tapatalk

  6. #6
    Regular Vistor
    Join Date
    Nov 2018
    Location
    Ontario, Ca.
    Posts
    16
    Yes, that's exactly how I've set it.

Similar Threads

  1. WAV doesn't connect via 1link to EB832
    By Eracerx in forum WAV Powerheads
    Replies: 1
    Last Post: 03-05-2022, 06:49
  2. Can't unplug wav pumps from 1Link port on EB832
    By layz79 in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 1
    Last Post: 06-04-2020, 12:01
  3. Help! 1Link on EB832 Question
    By SurlyTx in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 1
    Last Post: 05-31-2019, 11:05
  4. Question: EXTRA EB832 vs 1Link MODULE
    By MarineGP in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 12
    Last Post: 12-27-2018, 16:00
  5. Question: Do the EB832 1LINK ports have enough power for 1 WAV and 2 COR-15s?
    By jamesreich in forum EnergyBars 832 / 632 / 8 / 6 / 4
    Replies: 2
    Last Post: 08-24-2017, 14:30

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •