    ATK

    Has anyone had problems with there ATK. I’ve been in contact with apex on several occasions. For some reason it is just defaulting to off. And will not stay on auto. The eye is clean. The PMUP is in a 25 gallon barrel.
    Here is my programming
    Fallback OFF
    Set OFF
    If LoSump OPEN Then ON
    If MidSmp CLOSED Then OFF
    When On > 015:00 Then OFF
    Defer 000:10 Then ON
    Defer 000:30 Then OFF
    Min Time 030:00 Then OFF
    If FeedD 000 Then OFF

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    That means the pump ran for 15 minutes without the switch changing state and was shut to manual OFF as a safety precaution. You need to check all of the following.

    1. Do the opticals show CLOSED when actually covered in water

    2. Does the PMUP run when the ok Utley is set to manual ON

    3. Are there any clogs or pinches in the line

    4. Is the float set correctly so that it does not start reducing flow until the level reached the upper sensor.

    Sent from my SM-G965U using Tapatalk

  3. #3
    New User
    Join Date
    Feb 2018
    Location
    West Jordan Utah
    Posts
    5
    Yeah the optical sensor does work when covered in water. Yes I can turn it on manually and works just fine. And with that no kinks or clogs on the water line. And the float works great

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Then I would run it manually until the level is just below the low sensor. Then set to to manual OFF and then put it in AUTO and see if it starts cycling normally again. You might just be stuck in a loop where the water level is low enough to not fill in 15 minutes and by the time you notice it's in manual OFF enough water has evaporated to repeat the pattern.

    Sent from my SM-G965U using Tapatalk

  5. #5
    Frequent Visitor
    Join Date
    Mar 2015
    Location
    San Jose,CA
    Posts
    528
    How long is your FeedD?


    Sent from my iPhone using Tapatalk Pro

  6. #6
    New User
    Join Date
    Feb 2018
    Location
    West Jordan Utah
    Posts
    5
    5 minuets

  7. #7
    Frequent Visitor
    Join Date
    Mar 2015
    Location
    San Jose,CA
    Posts
    528
    What did support say?


    Sent from my iPhone using Tapatalk Pro

Similar Threads

  1. Help! ATK 'Error on ATK'
    By cottagereefere in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 2
    Last Post: 01-26-2020, 11:15
  2. Can the ATK be run with the PMUP plugged into a DC24v port instead of powering the ATK with AC?
    By powers2001 in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 7
    Last Post: 11-29-2018, 17:41
  3. Help! ATK PMUP fails to start ATK RELAY just CLICKS
    By AES in forum Fluid Monitoring Module (FMM), FMK, ATK, LDK, and FMM Accessories
    Replies: 4
    Last Post: 11-22-2018, 19:36

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •