    controller or PM2 connector for temp probe

    Recently upgraded from a classic to an EL - and re-used my PM2 with the EL.

    Is there any advantage of running two temp probes (one connected to the PM2 and one connected to the EL)? If I only use one - which should I connect to - the PM2 or the EL. I also have the salinity probe (connected to the PM2).

    Thanks!

  2. #2
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    There is benefit to using multiple probes particularly if you have a combination of in tank (or in overflow) and in sump heaters to provide redundancy in the event of a return pump failure. It can be very useful to have knowledge of both tank and sump temperature.

    If you choose to only use 1 temp probe, it needs to go in the PM2. Regardless of whether you use 1 or 2 temp probes, the temp probe plugged into the PM2 should be located as close as possible to the cond probe, preferably within a few inches of it so that temp compensation can be as accurate as possible.

    Sent from my SM-G965U using Tapatalk

  3. #3
    Frequent Visitor
    Join Date
    Nov 2013
    Location
    Michigan
    Posts
    171
    Thanks - I use the Neptune 4-probe rack in my sump - currently with salinity, temp and pH. I pulled my ORP from my base classic setup when I installed the EL.

    Now that I have 2 temp probes (original and the one that came wiht the EL) - I might set up the 2nd one in one of the overflows in the DT.

    If I do that - thoughts on whether or not the PM2 or head unit should be in the fuge (where the salinity probe is at)?

    Thanks!

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Detour View Post
    Thanks - I use the Neptune 4-probe rack in my sump - currently with salinity, temp and pH. I pulled my ORP from my base classic setup when I installed the EL.

    Now that I have 2 temp probes (original and the one that came wiht the EL) - I might set up the 2nd one in one of the overflows in the DT.

    If I do that - thoughts on whether or not the PM2 or head unit should be in the fuge (where the salinity probe is at)?

    Thanks!
    The PM2 temp probe should be in the sump next to the cond probe. And for the heaters I like to do this.

    Sump heaters run based on the overflow temp probe when the return is on and the sump temp probe when the return is off or if the overflow probe is obviously wrong (like readings less than 70 or over 90).

    Tank/overflow heaters run off the sump temp probe when the return is on and the overflow temp probe when the return is off or if the sump temp probe is obviously wrong.

    Sent from my SM-G965U using Tapatalk

  5. #5
    Frequent Visitor
    Join Date
    Nov 2013
    Location
    Michigan
    Posts
    171
    Thanks Zombie -

    Do you have an example of the code you use for the sump heaters that behave one way using the overflow temp when return pump is on, and another way using the sump temp when the return pump is off?

  6. #6
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by Detour View Post
    Thanks Zombie -

    Do you have an example of the code you use for the sump heaters that behave one way using the overflow temp when return pump is on, and another way using the sump temp when the return pump is off?
    Like this

    TankHeatNor (VO)
    If SmpTmp < 77.8 Then ON
    If Output Return = OFF Then OFF
    If SmpTmp > 78.0 Then OFF

    TankHeatPrb (VO)
    If TnkTmp < 77.8 Then ON
    If Output Return = ON Then OFF
    If TnkTmp > 78.0 Then OFF

    SumpHeatNor (VO)
    If TnkTmp < 78.0 Then ON
    If Output Return = OFF Then OFF
    If TnkTmp > 78.2 Then OFF

    SumpHeatPrb (VO)
    If SmpTmp < 78.0 Then ON
    If Output Return = ON Then OFF
    If SmpTmp > 78.2 Then OFF

    TankHeater
    Fallback ON
    Set OFF
    If Output TankHeatNor = ON Then ON
    If Output TankHeatPrb = ON Then ON

    SumpHeater
    Fallback OFF
    Set OFF
    If Output SumpHeatNor = ON Then ON
    If Output SumpHeatPrb = ON Then ON
    If SmpTmp < 70.0 Then OFF


    Sent from my SM-G965U using Tapatalk

  7. #7
    New User
    Join Date
    Apr 2019
    Location
    WEST PALM BEACH, FL
    Posts
    1
    When connecting the temperature probe to the PM2 unit can it still be used to control the chiller?

Similar Threads

  1. HELP - New temp probe connector not connected?
    By Agiacosa in forum A2 Apex/ApexEL and A3 Apex Pro/Apex/Apex Jr
    Replies: 2
    Last Post: 08-24-2019, 08:37
  2. Replies: 2
    Last Post: 08-15-2019, 08:05
  3. Factory temp probe(temp)and pm2 (tempx4)probe calibration
    By clarksski in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 1
    Last Post: 09-09-2015, 13:12
  4. Can I forgo the base temp and just use PM2 temp probe?
    By highergroove in forum Misc Apex Usage & Programming
    Replies: 2
    Last Post: 01-31-2015, 13:11
  5. Question: Temp probe of Apex module and temp probe of PM2 (salinity) give different readings
    By Klaas Oreel in forum AquaBus Modules, Probes, and Breakout Boxes
    Replies: 2
    Last Post: 08-03-2013, 17:06

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •