    Max gyre alarm messages

    Hello guys, I’m getting multiple alarm messages for my Mac spec gyre pumps. The alarms seem to happen every minute or so once they start. First one I will get will say set off. Next it will say if output max gyre pump amps <0.1 then on. Has anybody ever seen this?

  2. #2
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,489
    Don’t use Amps - use watts. The Gyres don’t draw enough power to effectively use amps to sense an abnormal condition.

    It’s possible that your programming results in the speed of the pump to go down, thereby using less than 0.1A of power at those moments in time.

    Post the programming for the Gyre and all pertinent alarms settings.
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  3. #3
    Regular Vistor
    Join Date
    Jan 2017
    Location
    az
    Posts
    25
    Quote Originally Posted by RussM View Post
    Don’t use Amps - use watts. The Gyres don’t draw enough power to effectively use amps to sense an abnormal condition.

    It’s possible that your programming results in the speed of the pump to go down, thereby using less than 0.1A of power at those moments in time.

    Post the programming for the Gyre and all pertinent alarms settings.
    NICE! I don't remember setting this feature up. How do I changed the alarm from amps to watts?

  4. #4
    Frequent Contributor zombie's Avatar
    Join Date
    Dec 2013
    Location
    Denver, CO
    Posts
    13,176
    Quote Originally Posted by dasidius View Post
    NICE! I don't remember setting this feature up. How do I changed the alarm from amps to watts?
    Inputs tab

    Sent from my SM-G965U using Tapatalk

  5. #5
    Regular Vistor
    Join Date
    Jan 2017
    Location
    az
    Posts
    25

  6. #6
    Regular Vistor
    Join Date
    Jan 2017
    Location
    az
    Posts
    25
    I think I fIxed it by turning off the Amps notification tab. There is still a watts tab that is set to recommended values. Is that all I had to do?

Similar Threads

  1. alarm messages- newbie questions
    By yraveh in forum APEX Fusion
    Replies: 0
    Last Post: 12-09-2019, 08:24
  2. Personalised alarm messages
    By Iain3 in forum APEX Fusion
    Replies: 2
    Last Post: 11-17-2019, 16:27
  3. Using standard ATO program, keep getting alarm messages.... ?
    By Charlie denmark in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 5
    Last Post: 06-14-2018, 08:04
  4. Replies: 6
    Last Post: 02-28-2018, 11:47
  5. Question: Maxspect Gyre 2nd Gen Pump/Icecap Gyre Int. Mod.
    By iamchadster in forum Apex Programming for Vortech, Tunze, & Other Controllable Pumps
    Replies: 13
    Last Post: 09-07-2017, 18:04

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •