Guys,
Little help, I've new reef sump and it's been difficult to maintain the same level of my ATK.
Most of the time the ATK put more water that needed and I'm getting a lot of alerts.
The sensors are positioned correctly.
This is my program for ATK
Fallback OFF
If ATKLOW OPEN Then ON
If ATKHIG CLOSED Then OFF
If LEAK CLOSED Then OFF
If Power Apex Off 001 Then OFF
When On > 002:00 Then OFF
Defer 008:00 Then ON
Defer 000:30 Then OFF
Min Time 120:00 Then OFF
This is my e-mail alert program
Set OFF
If Error ATK_PUMP Then ON
If ATKHIG CLOSED Then ON
If LEAK CLOSED Then ON
If Error VORTECH1 Then ON
If FeedA 000 Then ON
If Power Apex Off 001 Then ON
Thanks guys