Hello,
I'm running two heaters and wanted to have an alert if one of them stopped working. So, if one was on but drawing no voltage.
Hello,
I'm running two heaters and wanted to have an alert if one of them stopped working. So, if one was on but drawing no voltage.
If Output Heatername Watts < X Then ON
Where X is about 75% of it's normal wattage draw
Sent from my SM-G965U using Tapatalk
Hello, if I have the heaters on two cycles how would I update the code?
Alarm Code:
If Output Heater1 Watts < 175 Then ON
If Output Heater2 Watts < 100 Then ON
Heater Code:
Heater 1:
Fallback OFF
If Time 21:00 to 08:59 Then OFF
If Tmp < 78.0 Then ON
If Tmp > 78.3 Then OFF
Heater 2:
Fallback OFF
If Time 09:00 to 20:59 Then OFF
If Tmp < 78.0 Then ON
If Tmp > 78.3 Then OFF
It looks like you are trying to do my dual heater program. You have the time statements in the wrong place. Here's the thread with the current version of that programing.
https://forum.neptunesystems.com/sho...Heater-Program
Well, the question is really around the alert, not the dual program. I'll try this and see if ti works.
The idea is the alert won't alarm while the heater is in it's off period as it would be expected to draw zero watts.
Set OFF
If Output Heater1 Watts < 175 Then ON
If Time 09:00 to 20:59 Then OFF
If Output Heater2 Watts < 100 Then ON
If Time 21:00 to 08:59 Then OFF
This unnecessary. The Apex already handles this situation for you.
Power consumption alarm options and programming statements will be ignored if the specified output is manually OFF or the output is in AUTO and the output state is OFF due to programming. This behavior prevents false alarms about low watts or amps when an EB832 output is OFF.
As an example, let’s say that you have your return pump output programmed to turn the pump off while FeedA is active (If FeedA 000 Then OFF). You would not want an alarm about your return pump drawing 0 watts while your FeedA Cycle is active and the return pump is shut off. A watts reading of 0 is normal while the return pump is OFF in this case, so the Apex takes this into account, and will not trigger an alarm because the watts measurement is expected to be zero.
Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.
Yeah well, I tried it and it keeps setting off alarms even when it was off cycle.
I came up with the following which seems to work.
Set OFF
If Output Heater1 Watts < 175 Then ON
If Time 09:00 to 20:59 Then OFF
If Output Heater2 Watts < 100 Then ON
If Time 21:00 to 08:59 Then OFF
The issue with that is you would never get an alert between 21:00 and 8:59. Programs evaluate every line from top to bottom and the outlet sets to whatever the state is at the end. The last line would shut it off no matter what between those times. You can do this with 2 virtual outlets instead of trying to do it all in one.
As nicholb pointed out, the program logic here is incorrect, and will not do what you want it to do., But the greater issue is that you are trying to fix a problem that isn't being caused by what you think it is. The behavior of the If Output output-name Watts < ### Then ON is as I described -- the If Output output-name Watts < ### Then ON statement will not be TRUE if the referenced EB832 output is OFF (either manual OFF or OFF due to programming)
There is even a delay built into the underlying logic that gives allows several seconds after the EB832 outlets gets turned on for the device plugged into the EB832 to come up to speed (for example, a AC-powered pump) before the If Output output-name Watts < ### Then ON statement could become TRUE.
There is something else going on.
- What heaters do you use?
- Do they have internal thermostats?
- Are you using any external temperature controllers, like Inkbird or Ranco?
Lastly, did you fix the programming error nicholb had previously pointed out:
You had:
Heater 1:
Fallback OFF
If Time 21:00 to 08:59 Then OFF
If Tmp < 78.0 Then ON
If Tmp > 78.3 Then OFF
Heater 2:
Fallback OFF
If Time 09:00 to 20:59 Then OFF
If Tmp < 78.0 Then ON
If Tmp > 78.3 Then OFF
It should be:
Heater 1:
Fallback OFF
If Tmp < 78.0 Then ON
If Tmp > 78.3 Then OFF
If Time 21:00 to 08:59 Then OFF
Heater 2:
Fallback OFF
If Tmp < 78.0 Then ON
If Tmp > 78.3 Then OFF
If Time 09:00 to 20:59 Then OFF
Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.