    ATO Reservoir Help

    Hey guys,
    New to apex so I would appreciate if anyone could help me program my reservoir to fill up automatically.
    I have two sensors: ATO_LW and ATO_HI as well as the solenoid valve names ATO_SOLENOID.
    Trying to get the solenoid to open when water level hits the low sensor and turn off only when it reaches the high sensor.
    Im assuming its a simple task to create but for some reason i can't make it happen since it turns on when water level is low but then the solenoid closes as soon as the low sensor is closed (meaning it only fills up to the low sensor every time just a little of water is out).
    Any help is appreciated.
    Thanks

  2. #2
    Master Control Freak RussM's Avatar
    Join Date
    Dec 2012
    Location
    California - US Pacific
    Posts
    22,489

    ATO Reservoir Help

    Whenever asking for assistance with modifications to programming, always try to provide information up front that will help others help you in return.... such the programming that is not working as expected.

    In this case I can probably guess that you have a Set OFF statement in the ATO_SOLENOID program. If so, remove that line.

    There's a sticky post here that goes into depth about when and when not to use a Set statement: https://forum.neptunesystems.com/sho...l=1#post114462
    Please do not send me PMs with technical questions or requesting assistance - use the forums for Apex help. PM me ONLY if the matter is of a private or personal nature. Thanks.

  3. #3
    New User
    Join Date
    Nov 2018
    Location
    Florida
    Posts
    2
    Noted, will do!
    As far as my question, removing the Set statement did the trick.
    Thanks for the help and advice!!

Similar Threads

  1. Review My Program ATO Reservoir
    By Bada Bing in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 8
    Last Post: 04-13-2022, 13:30
  2. Help! Shut off my ATO pump once my ATO reservoir runs dry.
    By sirrichard33 in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 2
    Last Post: 02-15-2020, 11:28
  3. Question: FMM/ATO issues when ATO reservoir is refilled
    By Faulker's Maze in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 12
    Last Post: 12-14-2018, 11:43
  4. ATO for RO reservoir
    By fruth2000 in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 0
    Last Post: 06-23-2015, 05:20
  5. ATO Reservoir
    By Raul-7 in forum Apex Programming for Dosing, ATO, and AWC
    Replies: 16
    Last Post: 04-11-2015, 15:09

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •