Originally Posted by
zombie
I would do this actually. This will run a reduced speed for up to 2 minutes and if the level is still low, it will shut the LowSumpLO VO to manual ON, which will hold the pump off until you intervene.
LowSump
Set OFF
If Switchname OPEN Then ON
Defer 000:10 Then ON
Min Time 001:00 Then ON
LowSumpLO
Set OFF
If Switchname OPEN Then ON
Defer 002:00 Then ON
Defer 000:10 Then OFF
When On > 000:02 Then ON
COR
(Existing code)
If OutputLowSump = ON Then X
If Output LowSumpLO = ON Then OFF
Email
(Existing code)
If Output LowSumpLO = ON Then ON
Sent from my SM-G965U using Tapatalk