Dosing – Calcium and Alkalinity
This example shows two separate dosing outlets called Calcium and Alkalinity. The Calcium outlet runs for 3 minutes 20 seconds each hour except during the day (lights = ON), during a FeedA cycle or if the pH is > 8.35. The Alkalinity runs the same except is offset by 30 minutes from the Calcium
[Calcium]
Fallback OFF
OSC 000:00/003:20/057:40 Then ON
If Outlet [Lights] = ON Then OFF
If pH > 8.35 Then OFF
If FeedA 000 Then OFF
[Alkalinity]
Fallback OFF
OSC 030:00/003:20/027:40 Then ON
If Outlet [Lights] = ON Then OFF
If pH > 8.35 Then OFF
If FeedA 000 Then OFF