The following code will keep your tank temperature between 79 and 80 year round.
[Chiller]
Fallback ON
If Temp > 80.0 Then ON
If Temp < 79.5 Then OFF
[Heater]
Fallback ON
If Temp < 79.0 Then ON
If Temp > 79.5 Then OFF
If Temp < 70.0 Then OFF <-- this is in case the temp probe fails and gives you a false reading
Here's a way to visualize the integrated Heater and Chiller program above:
79.0 79.5 80.0
| | |
|------- HEAT -----------------|------- CHILL ---------------|
0N OFF ON
The heater will turn on at 79 (actually 78.9) and heat until the water rises to 79.5 (actually 79.6) then turn off.
The chiller will turn on at 80 (actually 80.1) and cool until the water cools to 79.5 (actually 79.4) then turn off.
If you have a heater with its own t-stat, you would set that t-stat to maintain a temp just slightly warmer than 79.5.
If you have a chiller with its own t-stat, you would set that t-stat to maintain a temp just slightly cooler than 79.5.
This way even if the Apex fails to turn off the heater or chiller, their own internal t-stat will turn them off. And by setting their t-stat to just slightly warmer/cooler than 79.5, you're insured they will always turn ON when the controller wants them to be ON.